Mend Worcester 24i Boiler Hot Water Heat Exchanger

Why is my water still to hot?

Previous Q & A :-
I have a recently installed worcester 24i (LPG). The tap water gets very hot and after a while runs cold, read it should be limited to 55*?

your heat exchanger may be scaled up, especially if in a hard water area. either that or the dhw sensor is faulty.

Had the worcester engineer out. He changed the dhw sensor and set the boiler up correctly (said it hadn't been). He told us it should now be ok, but mentioned that if not it would be because the incoming water pressure is to low and there was not much we could do about that. Needless to say the problem has not been resolved. We don't live in a hard water area and it's a new boiler so can't see the heat exchanger being scaled up. Is the engineer right about the water pressure or could there be another fault?

Steve B
October 2009
the problem is not water pressure but water throughput, (or flow rate), when the water becomes too hot you manually increase the cold water and decrease the hot water flow. this trips a safety protection. the solution is to change the mixing battery to old fashion battery with 2 different taps so you can leave the hot water allways high and add cold water as much as you need, I had that problem.

guido
November 2009
Water pressure is always a problem with combis and should really have been checked by your installer before installation, with a water gauge.
One thing you could try is make sure your main stop cock is fully open,you may also have one outside in the footpath again check fully open.Is your water supply shared with your neighbours? Ask you local water company if there is reason for poor pressure.
Sorry can't be more help than that.

Glen
October 2009

Automatic Answer

We may have found other answers which could help you.

Click here for Boiler Hot Water Heat Exchanger

Related Questions ...

Mend boiler heating system failure
2

Is my boiler a write off?

My 8 year old Baxi 105he appears to have a crossover between the hot water and heating system. When the heatin... [Read more]
Mend pressure worcester heat
1

Faulty Worscester 35 CDi loosing pressure?

My Worcester 35cdi has had 4 replacement heat exchanger's in less than 10 years the first 2 were within the fi... [Read more]
Mend boiler radiator heat exchanger
1

help how to fix or sort radiator downstairs being cold?

Glowworm beatacom 30c.2 rads upstars get hot both sides fully.but one downstairs cold.drained systym fully.ref... [Read more]
Mend boiler heating fault
2

Potterton Performa 24 DHW issues?

My Potterton Performa 24 has developed a DHW fault, & I need help resolving it please. In November, it stoppe... [Read more]
Mend heating boiler valve
3

Glow-worm 30cxl?

Started off blowing 3amp fuse in boiler, water cold but heating working ok, engineer came out and fitted a ser... [Read more]
Mend central heating going
3

central heating works fine, but hot water keeps going on and off?

i have a ariston eco 35mffi c ombi boiler.The central heating works fine,but the hot water(dhw)starts fine, th... [Read more]
Mend vaillant changed diverter valve
1

how can i fix my boiler?

i have a vaillant turbomax 242e changed diverter valve but still not getting hot water .gasman told me dhw hea... [Read more]
Mend combi heat exchanger sensors
6

Ideal Combi Logic boiler "L3" fault. ?

Whenever the temperature knob is turned up higher than half way, the boiler shuts down, flashing L and 3. Have... [Read more]
Mend heating heat exchanger boiler
1

Ideal HE24 Isar?

i have an ideal he24 isar boiler with the fault l-9 the plummer told me i have to change the heat exchanger ... [Read more]
Mend 30 problem heat
2

glowworm betacom 30 problem?

Hello folks, boiler is 2 years old, had plate heat exchanger cleaned/changed/cleaned...dhw sensor replace... [Read more]
Mend expansion tank hot
1

Expansion tank hot?

Greenstar Ri boiler open vented system. When boiler switched on constant flow of hot water to expansion tank... [Read more]
Mend How to mend it?
1

How do i solve a Remeha Avantaplus E7 fault code?

My boiler is approx 6yrs old and has now stopped supplying hot water after an E7 error code. The central heat... [Read more]
Mend boiler combi heating
1

water going hot then cold?

vaillant combi boiler 824/2e ,,heating is fine,hot water red hot then goes cold had new heat exchanger,plus ne... [Read more]
Mend boiler heating heat exchanger
1

Halstead issues?

Have a Halstead Quattro with domestic water problems. Have fitted new diverter diaphram and heat exchanger, so... [Read more]
Mend heating flow switch heat exchanger
1

halstead ace high boiler?

Hi after reading some of the posts on this website which were having the same problem as me (boiler playing up... [Read more]

How to mend ...

Find out how to mend just about anything howtomendit.com for free repair help, information and advice.
Mend Home Heating Systems ...