The fan on my 20 year old Prima 60F boiler gave up a couple of weeks ago with seized bearings causing the boiler not to fire up. I took the unit out and managed to free it up, but thinking that would just be a temporary fix, I ordered a new one along with the two fibre gaskets, the originals having disintegrated during removal of the fan unit.
Having fitted the new fan unit, I found that ignition was intermittent and mostly when the boiler was starting from cold, but could be started by thumping the casing. I had had previous trouble with dry joints on the connector at the front of the electronics board so I decided to remove it and check for more dry joints. I couldn't see any so I did a Google search and found this thread and learned about the three capacitors, which I then bought (100C, 100V versions) from Maplin, fitted and re-fitted the electronics board.
This time I had trouble with the fan powering up and down every couple of seconds, so I ordered a new pressure switch and fitted that. The fan powered up properly but the ignition was still intermittent and I discovered that by tapping the metal tray on which the electronics board is mounted, a spark would be generated. Out with the board again and a detailed inspection of the solder joints with a magnifying glass and there it was! The output pin from the spark transformer had a dry joint; it looked OK at first glance but by pulling and pushing on the transformer casing, the pin could be seen moving up and down in the solder. A quick dab with the soldering iron on that joint and a few others just to be sure; back with the board and bingo,the boiler worked perfectly.
So some things to look for based on my experience:-
1) The spark between the electrode and the shield should be a long yellowish arc connecting both. If the spark is bluish-white and about the size of a pinhead located in the gap, then there is something wrong with the spark generation electronics.
2) If the pilot light does not ignite immediately, the spark should repeat every one to two seconds. If it does not do this, there is something wrong with the spark generation electronics.
3) If thumping the case, or tapping the metal tray with a heavy object, such as a screwdriver handle, causes the boiler to ignite, there is something wrong with the electronics board, most probably a dry joint.
4) If intermittent ignition occurs, primarily when the boiler is attempting to fire from cold, then there is something wrong with the electronics board, most probably a dry joint.
5) If the fan only spins up for a couple of seconds and then stops and the cycle repeats, suspect the air pressure switch.
After all the faffing about, I am expecting another 20 years out of this boiler and the electronics board is probably working better and is more reliable than when the boiler was new. The soldering quality was abysmal!
Total cost: £120 for the fan unit, £8 for the fan unit gaskets, £50 for the pressure switch and a few pence for the capacitors.
Many thanks for all the info from the others that have contributed to this thread, especially about the capacitors.
TAM
September 2014