i had the same problems as above.
sabre 29he runs the central heating for 10 mins then cuts out and displays red led.
actual symtom was, CH would run until it got upto temp then cut off, but the boiler wouldnt re ignite when the temp dropped again. i bought a new NTC sensor off ebay for £5.80, but it didnt cure the fault.
i discovered that the boiler would reignite when hot if i undid the clips on the siver panel with the glass window and it sucked some air in. further to that i discovered it was the pressure switch at the top which wasnt operating when the fan started and the boiler wanted to ignite, but would if the silver panel was unclipped.
i had found a thread on this site that said 'if the venturies were dusty it would cause this fault'. so i cleaned the venturies with a cotton bud. the lower venturie (on the fan housing in the top right of the boiler connected with clear tubes) is a straight pipe, so is easily cleaned with a cotton bud, and the cotton bud was dirty from cleaning this. but the problem comes with the upper ventury as this has a 90 degree bend inside the fan housing, after cleaning with a cottonbud i reassembled the boiler and now it wouldnt fire up at all.
i had to remove all relivent screws holding the hood and fan motor, and pull hood out about 3" so could put two fingers in the fan housing and take the upper ventury out (after unscrewing the brass retaining nut) and i discovered a blob of jointing compound just on the inside edge of it. this is down to poor assembly at the factory. the ventury was cleaned and boiler reassembled.
the boiler now fires up much much quicker then it ever did. meaning hot water as soon as the tap is switched on and no more red led.
toasy warm, north lincs.
September 2009