Mend > Home Heating Systems

Mend Baxi 105 HE Boiler Pressure Heating

re pressurizing my Baxi 105 HE?

I removed a radiator in my lounge so that the room could be plastered.
I refitted the radiator afterwards but of course the boilers pressure read "0" I followed the installation instruction on "commissioning the Boiler" : Filling loop fitted and open ( valve handle at 90 degrees, heating flow and return valves open (I think these are the two valves to the righthand side underneath the boiler). Open the screw on the automatic air vent but nothing happened. Have I missed something ?

Ian Douglass
July 2008
The automatic air valve is what it says " automatic " and has nothing to do with you re-pressurizing the system.
Assuming the radiator has been fitted back onto its pipework and the radiator bleed valve is closed. Open the two valves either end of the radiator. Open the filling loop taps and when the pressure gauge reaches 1 1/2 bar on the gauge close the filling loop taps.

DO NOT START YOUR BOILER AND THE PUMP YET

Next start bleeding your radiators starting with the ones downstairs. As you bleed air from a radiator tighten the bleed screw every now and then and check the pressure gauge ( NEVER LET IT REACH 0 ) if it has fallen slightly open the supply loop taps until the pressure gauge reads 1 1/2 bar on the gauge. Continue bleeding air from all the radiators ending with those upstairs ( air rises to the highest point in the system ).
When you have bled all the air out of your radiators open the bleed screw on the radiator nearest the boiler and allow water out of this bleed screw until the pressure gauge on the boiler reads 1 bar ( this is a standard pressure fore most combi boilers ).

You can now switch on the boiler and the water should circulate around the system ( because some air could have been trapped by bends in the pipework etc you may find it necessary to re-bleed the system in a few days ) , you will notice the pressure gauge reading will drop if this needs to be done.

The point of having an automatic air vent is to provide a means of ridding the sealed pipe system of any dissolved air within the water. ( If you boil an egg in a pan you will see air bubbles liberated from the water, when it is heated . The same happens in the sealed pipework of the CH system, the automatic air vent gets rid of this however the pressure within the system will then fall and you will need to open up the filling loop and pressurize the system to 1 bar again.

Every week check you boiler pressure and re-pressurize as required

If the tops of your radiators are cold whilst the bottoms are hot then you have air in the top half of your radiators and they need bleeding.

If the tops of your radiators are hot but the bottoms are cold, you have a build-up of sludge or rust in the radiators. The radiators can be removed and should either be flushed clear or replaced.

If either of these situations arises the system will again need re-pressurizing to 1 bar.

John ( Wirral )
August 2008
it possible that the check valve is wrong way stopping it from filling

summy
July 2008
have you managed to pressurse your bolier, i have the same problem - can someone help me also.
Bali

Bali
July 2008

Related Questions ...

Mend baxi boiler 105e
1

Power but not activating Baxi 105e boiler?

My brother lives away and he asked me to go round and turn on his Baxi 105e boiler. I've turned the power on a... [Read more]
Mend boiler heating pressure
2

Potterton Perfoma 24. Hot water works fine No heating?

Hi, I have a Potteron Perfoma 24 boiler. The heating has stopped working Hot water is working fine. I've trie... [Read more]
Mend boiler pressure radiators
1

over pressure?

I have a greenstar 24i boiler, pressure is normal, when I turn heating on pressure increases and eventually op... [Read more]
Mend boiler heating Vaillant
1

how to fix water pressure its down at bottom of grey part?

the heating and hot water working but pressure looks to low Vaillant ecoTEC condensing boiler
Mend boiler heating system failure
2

Is my boiler a write off?

My 8 year old Baxi 105he appears to have a crossover between the hot water and heating system. When the heatin... [Read more]
Mend pressure heating expansion vessel
1

pressure and heating keeps going off?

my boiler keeps loosing pressure and going to 0 there is no leak in the house and no water coming out the pipe... [Read more]
Mend boiler radiators pressure
2

I only have heating downstairs... ?

Hi all. My heating has been a bit funny. The radiators upstairs aren't heating up at all and the ones downstai... [Read more]
Mend boiler condensing boiler faulty
2

Faulty Ravenheat condensing boiler?

My Ravenheat CSI primary condensing boiler will not fire up. I called out a heating engineer who diagnosed a f... [Read more]
Mend boiler pcb condensate
1

Faulty vokera compact 25?

I have spoken to the gas safe engineer that installed this boiler new approx. 3 years ago about the problems i... [Read more]
Mend boiler pressure blockage
2

Worcester 24i combination boiler pressure loss?

Had fan changed, PCB board changed, internal blockage due(manifold changed) water pressure sensor changed. N... [Read more]
Mend boiler heating error code
2

how to fix f22 problem on boiler?

I don`t have a combi boiler but i do have a f22 problem.The pressure is fine but when i switch the water on,th... [Read more]
Mend boiler pressure diverter valve
1

how can i fix my baxi 105HE?

my boiler water pressure keeps on goin up to nearly 3bar and expelling alot of water outside.CH works when i ... [Read more]
Mend boiler pressure heating
1

vokera boiler not 2yrs old yet , wont work?

the red light is staying on which is not a good sign, have managed to get pressure gauge to normal level as ... [Read more]
Mend boiler heating breakdown
1

What is wrong with our boiler? Had several repairs?

Our boiler broke down just 6 months ago where we had it repaired and the switchboard changed. A year before th... [Read more]
Mend gas boiler thermostat hot water
2

Glowworm cx30i gas boiler?

My boiler comes on intermittently when the thermostat is turned down below zero degrees. It is all running fi... [Read more]

How to mend ...

Find out how to mend just about anything howtomendit.com for free repair help, information and advice.
Mend Home Heating Systems ...